Re: Solar PV Production
« Reply #210 on: July 03, 2015, 10:48:37 pm »
Sorry to hear of the problem but a big thanks for posting it as all ofnus could have probs at any time.
 
My mate Stewart has recently seen the  EB change the local failing transformer PDQ , as it was kicking out over 280 volts. Initially the EB said nothing was wrong.

 They are hoping to get recompensed for two months loss income as their control panel kept dropping out many times a day  . He's using the average generation of March & April over the last three years 2012 -2014  in support of his claim. 
Strong belief , triggers the mind to find the way ... Dyslexia just makes it that bit more amusing & interesting

honeyend

  • Joined Oct 2011
Re: Solar PV Production
« Reply #211 on: July 22, 2015, 12:39:05 am »
 :sunshine:
 My husband checks all the readings and is not very good at keeping a record apart from when he sends it in. Today I got him to read the leccy metre to see how much we have used, after much nagging, and we are producing more than we use.
 We have an air source heat pump which has not heated the house since April, it does the hot water, all bulbs apart from about 4 are led, and daughter has moved out so it should go down even more. So we are making money!!! Well not spending it.:sunshine:

Sudanpan

  • Joined Jan 2009
  • West Cornwall
    • Movement is Life
Re: Solar PV Production
« Reply #212 on: July 22, 2015, 08:43:02 pm »
We are still having a torrid time with our inverter. First of all the installers changed the inverter (a Samil Power inverter) but this made no difference. Then they upped the settings parameters (currently as soon as our panels generate about 4kw the grid voltage side goes up to 265V and the inverter disconnects) - so they upped the upper level to about 270V but this has not made any difference.
So, apparently now the next stage is to get Western Power involved - but no idea what that is going to entail.
Not exactly what we envisaged when buying into the PV panel setup.
 ???

cloddopper

  • Joined Jun 2013
  • South Wales .Carmarthenshire. SA18
Re: Solar PV Production
« Reply #213 on: July 23, 2015, 11:34:43 pm »
It took me several weeks  till i eventually got the address of the local area's certified  electrical engineer for our electricity board . Once I laid out my problem as I saw it and added all manner of pertinent notes , I asked him to come and visit me face to face with one of their senior testing engineers such as a foreman so we could talk the problem through.
 Two days after that comunication he and his assistant visited me . They made some very useful comments which I sent on to my insurers wrt lightening strikes within 400 mtrs of my home ( the insurers had refused to acknowledge these at the time as no one else had made  a claim  )
End result nearly six months later I got several thousands pounds of insurance claim to pay for my losses.

Do you have any recorded date of when you found some thing wrong with your system ?
If so see if you have any locall weather station type enthusiasts who use the Norwegian lightening strike satelite data system and see if they can get dates of strikes , within say 800 mtrs of you during the period and about 15 days either side .
Strong belief , triggers the mind to find the way ... Dyslexia just makes it that bit more amusing & interesting

Big Light

  • Joined Aug 2011
    • Facebook
Re: Solar PV Production
« Reply #214 on: August 01, 2015, 08:55:44 am »
412 for July a good 130 down  :raining: :raining: :raining: :raining: :raining: :raining: :raining: :raining: :sunshine: :raining: :raining: :raining: :raining: :raining: :raining: :raining: :raining: :raining: :raining: :raining: :gloomy: :gloomy: :gloomy: :gloomy: :gloomy: :gloomy: :gloomy: :gloomy: :sunshine: :raining: :raining: :raining: :raining: :raining:

Loobylou

  • Joined May 2015
Re: Solar PV Production
« Reply #215 on: August 01, 2015, 07:37:03 pm »
I must admit I'm useless at remembering to give my readings. I've just given one and it's well overdue bug I'm well impressed with my payment.

Dan

  • The Accidental Smallholder
  • Administrator
  • Joined Oct 2007
  • Carnoustie, Angus
    • The Accidental Smallholder
    • Facebook
Re: Solar PV Production
« Reply #216 on: August 03, 2015, 10:17:52 am »
484 for July, down from 571 in 2014.  :(

 :fc: for  :sunshine: in August.

Greenerlife

  • Joined Mar 2009
  • Leafy Surrey
Re: Solar PV Production
« Reply #217 on: August 03, 2015, 05:14:55 pm »
Well don't feel too despondent Dan!  My reading for the 'sunny' south was 393!

Sudanpan

  • Joined Jan 2009
  • West Cornwall
    • Movement is Life
Re: Solar PV Production
« Reply #218 on: August 04, 2015, 08:21:42 pm »
Don't really have a clue what July's generation was as the changeover of the inverter etc has messed up the recordings. However, I do know that on days where we would have expected generation in the region of 30+kw we have only got 18kw because of the inverter constantly disconnecting and reconnecting. I reckon we will be down about 40% when all is said and done on what we should have generated.


Our installers have been monitoring the inverter loads and the corresponding grid voltages - basically the grid voltage ranges from the low 220's up to 270+. When our panels get to about 70% generation, without a drawdown due to demand on site, the grid voltage gets upwards of 260, tripping out at 265v.


They are going to be in further discussions with Western Power - but in the meantime their recommendation is to try and switch on as much stuff as poss when the sun is strong! I've looked into the possibility of an intelligent switch (ie immersun) to kick in when our generation gets up to 3kw and switch on some high load - however an immersion heater is not the answer as we are already drowning in hot water as we have solar thermal panels. We're thinking that maybe we should get some sort of storage heater in the garage or something - though it is irritating that we will have to fork out more money in order to stop our PV system from tripping out all the time.

cloddopper

  • Joined Jun 2013
  • South Wales .Carmarthenshire. SA18
Re: Solar PV Production
« Reply #219 on: August 09, 2015, 12:40:19 pm »
Sudanpan , have you put the problem & symptoms to the guys on the " Renewables " website ( I can't remember the actual website details ).  They gave me several useful ideas to mull over when i started out onn my renewable's quest  Knowing that there are so many fairly well qualified to comment guys using the site with real time knowledge might be to your advantage .
Strong belief , triggers the mind to find the way ... Dyslexia just makes it that bit more amusing & interesting

cloddopper

  • Joined Jun 2013
  • South Wales .Carmarthenshire. SA18
Re: Solar PV Production
« Reply #220 on: August 09, 2015, 12:54:36 pm »
Reading    31 Mar 2015       3807.12    =   259.99  produced
Reading    3  May 2015       4314.72    =   507.60  produced   
Reading    31 May 2015      4745.77     =   431.05  produced
Reading    30 Jun 2015       5336.11     =   590.34  produced
Reading     8 Aug  2015      5878.22    =   542.11  produced .. ( late July reading ..on holiday so let's call it as 515  units for July )

 The recent lousy weather certainly has had an impact  my garden is about three week behind .. so are the tomatoes etc.in the glasshouse.
UK grown veg might just be a bit more expensive over the next six months or so.
Strong belief , triggers the mind to find the way ... Dyslexia just makes it that bit more amusing & interesting

Sudanpan

  • Joined Jan 2009
  • West Cornwall
    • Movement is Life
Re: Solar PV Production
« Reply #221 on: August 10, 2015, 08:17:10 pm »
Thanks for the tip Cloddopper - have registered in the renewables forum and will see if I get any further pointers. One reply has suggested I take it up with the suppliers (Western Power) as the voltage range should be 230v + 10% (so 253v) top end which should be fine.

cloddopper

  • Joined Jun 2013
  • South Wales .Carmarthenshire. SA18
Re: Solar PV Production
« Reply #222 on: August 11, 2015, 11:33:20 pm »
That sound a bit like you are on a dirty branch line where the boards transformer is degrading..... every time there is a spike on the branch due to someone switching on or off heavy current you get the electrical echo of the spark jumping across the switch contacts .
 At our small farm  a simple lie detector type moving arm trace showed a steady 233 volts
 With some large digital storage device and a special dual trace beam oscilloscope  it showed that we were getting hit every few seconds most days between 07.00 hrs and 21 .00 hrs with spikes of over a thousand volt for a millisecond or slightly less. which kept tripping our breakers .

It turned out to be a small industrial machinist/welding unit who was working double shifts every time the struck or broke an arc we got tripped out.
 The incoming mains to our pole transformer we were both running from was also dirty so the industrial units welding  just amplified the mess  .
 
Strong belief , triggers the mind to find the way ... Dyslexia just makes it that bit more amusing & interesting

cloddopper

  • Joined Jun 2013
  • South Wales .Carmarthenshire. SA18
Re: Solar PV Production
« Reply #223 on: August 18, 2015, 01:16:47 am »
We are still having a torrid time with our inverter. First of all the installers changed the inverter (a Samil Power inverter) but this made no difference. Then they upped the settings parameters (currently as soon as our panels generate about 4kw the grid voltage side goes up to 265V and the inverter disconnects) - so they upped the upper level to about 270V but this has not made any difference.
So, apparently now the next stage is to get Western Power involved - but no idea what that is going to entail.
Not exactly what we envisaged when buying into the PV panel setup.
 ???

 I've been talking with Stuart the guy who had the transformer problem ..it turns out he's been fitting solar systems for quite a time ..(He showed me his notice letter  for £100.67 p for his last quarters FIT payment  He put it in when the FIT's were a lot more generous & it's certainly paid for itself said he grinning form ear to ear.

  I kind of described what i think you have been saying , his comment was , " Every system has to push electricity at a higher voltage into the mains .. this has the effect of causing the mains to rise by a volt or so . If you are on a branch line with a dozen other solar systems pushing power into the network you will see the mains voltage rise considerably . This can and does cause problems of so high a voltage that it trips solar panel rectifiers out .

Then he asked me to say to you , Do you get trip outs when it's dark ??
Strong belief , triggers the mind to find the way ... Dyslexia just makes it that bit more amusing & interesting

Sudanpan

  • Joined Jan 2009
  • West Cornwall
    • Movement is Life
Re: Solar PV Production
« Reply #224 on: August 18, 2015, 08:49:29 pm »
Then he asked me to say to you , Do you get trip outs when it's dark ??


We only get trip outs on the inverter itself so no we don't get trip outs when it's dark as the inverter is not working in any event.
The message we get from the inverter is that it detects a Grid Over Voltage so it disconnects and then takes 30 secs to reconnects.
Western Power came last week and has put a data logger on the line in so that should be able to be compared to what the inverter record is saying to determine more specifically where the issue lies

 