717 for June 2015 compared to 985 for 2014.......
This is all down to the inverter shutting down every 5 minutes when the sun is at its hottest because of the Grid overvoltage rating situation.
We've had our installers out a couple of times, they've taken lots of readings and been in discussion with Western Power and Samil (inverter manufacturers)
When the Grid voltage reading was hitting the 260v mark we switched on kettles etc to see what happened and yes the Grid Voltage reading would drop to 253v or so. LC said that it might be because we are at the end of our supply line and there's not a lot of electricity requirement from our locality during the day - up until Feb we did have a neighbour who ran a chocolate making company and had deep freezers etc running so the power requirement was higher - but they've left. In addition the people who have moved into their house have just installed their won PV array so potentially our problem may get worse

Samil suggested they changed the settings so that the upper limit (265v) was increased before the inverter shut down but ZLC said this was not acceptable so Samil have agreed to a new inverter - which we now have ready to be swapped over next week hopefully.
Gutting to lose nearly 300kw generation in a month